It is currently Fri Nov 06, 2026 6:10 am
 Post subject: ARCAD performance
PostPosted: Wed Feb 03, 2016 10:53 am
I am looking into doing an arc flash study of my plant. I have to develop a one-line and do an arc flash analysis for stickering. Has anyone experienced Arcad? Any input will be helpful.
Thanks in advance,
Kelly
 Post subject: Re: ARCAD performance
PostPosted: Thu Feb 04, 2016 8:07 am
Can you perform an ANSI or IEC short circuit calculation in detail with no assumptions (no infinite bus transformer primaries, no zero impedance conductors) correctly? Can you perform a TCC study based on the short circuit study? If the answer is yes then you have the prerequisites to use Arcad's web software. He has a lot of stuff on there. Some of it is based on somewhat more theoretical calculations and some of it is based on more empirical ones and standards. All are fairly well documented.
The short circuit and coordination studies are required by NEC Code which unlike 70E is state law in all 50 states and not just "required" indirectly. Most licensed electricians should be fully capable of doing an NEC grade "study" in a matter of minutes. But the nature of these studies is that there are some shortcuts which result in a "conservative" (over-estimate) result which is generally good enough to meet NEC requirements. But these same results cause the arc flash result to be underestimated.
In the case of >15 kV OSHA has more or less "blessed" ArcPro software with the revised 30 CFR 1910.269 rules, so you are probably best following their guidance. Read 1910.269 in the appendices for more information on this. From 250 V-15 kV currently the best documented/most reliable calculation is the IEEE 1584 empirical calculation. Below 250 V you are generally stuck using a table or research results since the calculation breaks down at that point. Since at least some of Arcad's calculations are based on IEEE 1584 then you can use those but again, you need a lot more information than just a one line.
If the answer is no then I offer you three solutions. The first one is to use the table method in 70E which means that you need to know the task being performed, the equipment being worked on, and third you need to know the short circuit and opening time of the equipment, in theory. If you've already done these calculations then you might as well do the engineering study approach since the PPE requirement will be much less among other reasons.
This is where Arcad and I have a difference of opinion. In the case that you don't have the engineering calculations, and as I'm hinting at there's a lot more than just arc flash, then using the tables without benefit of the calculations is better than nothing at all. In fact a study has been done that shows that "dumb luck" (not doing anything about arc flash) done by some folks at Dupont based on about 30-40 cases has a serious injury rate of 100%. If you just use the tables without the engineering calculations then based on an older edition of the tables (the 2015 version is much improved) there is a 50% chance of avoiding serious injury. And if you do the engineering calculations although there is a theoretical 5-10% chance of injury in practice it drops to 0%. So as much as I'd argue for the engineering study approach whether you use Arcad's web site or not, using the tables at least initially is better than doing nothing at all by a wide margin.
The second answer is to get the training to do the calculations. This is where since Jim Philips runs this web site and he does the training, it would only be fair that I mention him. Be sure you understand what the training is. Some trainers only do the electrical safety training which works alongside whatever shock and arc flash risk assessments and hazard assessments (they are two different things) that you've done. If you want to see an example of this, Terry Becker's web site although it doesn't do all of the training, is really good and representative of the training that needs to be done over and above the electrical hazard studies.
The third answer is to hire someone to do the calculations for you. But in this regard you are best off using a local source for a couple reasons. First there is quite a bit of on site inspection that goes along with doing a good electrical hazard study (arc flash and shock). I live in Eastern North Carolina so your travel expenses would be ridiculous if you tried to use my company to do an arc flash study for say Oregon.
The second reason for using someone local is that the study has to be revalidated every 5 years. And due to the rules for professional engineers if you switch engineers they also need to revalidate it. And every time you need to make changes especially adding equipment the study has to be revised to cover the changes. If you use the same contractor they can just go in and make the change in a few minutes and perhaps one site visit which is very cost effective. But again if your engineer is remote to the site, it is going to be an expensive relationship long term.
Along the way, be aware that there are several side benefits:
1. You will know your actual short circuit currents. This will most likely result in finding more than a few pieces of equipment that are under-rated.
2. You will know where your breaker/fuse settings are not adequate and can either cause nuisance trips or are not providing adequate protection.
3. You will know where your areas of miscoordination exist and how to address them (or live with them).
4. You will know what your equipment conditions are and where they need to be addressed.
5. You will know where you stand in terms of knowledge and work practices when it comes to electrical safety.
PostPosted: Fri Feb 05, 2016 9:19 pm
ARCAD's SCA V1.0 software program[/url] for short circuit fault current calculations is based on the comprehensive methodfor short circuit analysis, factors in both active and reactive parts of equipment impedance and takes into account contributions from multiple sources including motors and generators. The disparity between calculation results from ANSI, IEC comprehensive method etc. can be explained by different approximations and assumptions adopted by different methodologies. For example, some techniques ignore equipment X/R ratios in the analysis and apply different correction factors to equipment ratings. Disregarding the equipment X/R ratio introduces up to 15% uncertainty in a single step of adding two impedances alone while applying different correction factors does not quantifies and does not corrects the error but only amplifies it.
ARCAD's AFA V5.0 software program and mobile apps[/url] for arc flash hazard analysis and labeling are based on IEEE 1584 Guide for Performing Arc-Flash Hazard Calculations. The IEEE 1584 empirically derived model was chosen for arc flash analysis due to the model's capability to accurately account for a wide variety of setup parameters including:
* open and box equipment configurations
* grounding of all types and ungrounded
* gap between conductors of 1/8 to 6 inches
* bolted fault currents in the range of 700A to 106kA
* system voltages in the range of 208V to 15kV
* working distances from 10 to 80 inches
For cases where voltage is over 15kV (up to 46kV max) or gap is outside the range of the empirical model (more than 6 inches gap), IEEE 1584 recommends applying the theoretically derived Lee method and the method is also included in Arc-Flash-Analytic.
You may also consider ARCAD's for arc flash analysis in DC power system. Check for DC arc flash modeling implemented in DCAFA V3.0. The program calculation procedure[/url] is very similar to the procedure proposed by Jim Phillips in Know Your Arc: DC arc flash calculations. It also takes into account circuit time constant when determining arc duration as a function of predicted arcing current, upstream protection device type and rating and the fault time constant.
ARCAD has recently released new primary aimed for single phase arc flash analysis. Single phase AC tests on systems with an open-circuit voltage of 146V described in L. E. Fisher "Resistance of Low-Voltage AC Arcs" showed the arcing can continuously sustain even at this low value of voltage. ArcMaster's shows the arc voltage and arc sustainability depends on the circuit power factor. Note that both in theory and practice the arcing currents are dependent on system power factor when even a small change in the power factor may result in a significant change of arcing current. Namely, the tests tend to indicate weak unstable arcing at 100% PF but spectacular sustained arcing at low power factors at the same current and voltage.
I would not recommend using the NFPA 70E table method as I don't believe that encouraging your personnel working on energized equipment when there is 50% chance of serious injury is right. There are two methods to select the appropriate PPE.
1. Incident Energy Analysis OR
2. PPE Tables Method [130.7(c)(15)(A)(b) or 130.7(C)(15)(B) and 130.7(C)(16)]
An incident energy analysis shall be required in accordance with NFPA 70E 130.5 for the following:
1. Tasks not listed in Table 130.7(C)(15)(A)(a)
2. Power systems with greater than the estimated maximum available short circuit current
3. Power systems with longer than the maximum fault clearing times
4. Tasks with less than the minimum working distance
Hence, NFPA 70E prohibits using the PPE Table Method if short circuit fault current (2) and protection device operating time (3) is not know. Arcing current need be calculated in order to determine the upstream protection device operating time. Once, short circuit fault current, arcing current and arc duration have been calculated, incident energy and arc flash boundary for any tasks (1) and at any working distance (4) can easily be calculated using IEEE 1584 equations.
Michael Furtak, C.E.T.
http://arcadvisor.com
Hyperlinks to a commercial website and removed advertising paragraph
