arcflashprimero
|
Post subject: Does all equipment have SCCR? Posted: Wed Jun 10, 2026 3:14 pm |
|
Joined: Thu Dec 18, 2025 3:21 pm Posts: 18
|
|
Im relatively new to studies learning as I continue school.
When modeling equipment and checking submittals and spec sheets, I often find it hard to locate the SCCR. Does all equipment come with an SCCR? If not, would you use a default of 5k or 10k?
Specifically, at this moment I am modeling some power line filters for a data center job. I dont see any ratings for the power line filters beyond voltage, current, and hertz
what do you do if SCCR is not listed?
|
|
| Top |
|
 |
|
JBD
|
Post subject: Re: Does all equipment have SCCR? Posted: Mon Jul 06, 2026 9:29 am |
|
Joined: Mon Jan 18, 2010 11:35 am Posts: 615 Location: Wisconsin
|
|
I would use 5kA for hardwired devices. I think this is the default value that UL assigns to electronics like VFDs.
|
|