It is currently Wed Oct 28, 2026 10:10 am



Post new topic Reply to topic
Author Message
 Post subject: Rigid metal conduit used as fuses
PostPosted: Fri Mar 01, 2019 11:59 pm 
User avatar

Joined: Thu Feb 21, 2019 8:59 am
Posts: 46
Location: Boston, Massachusetts 02113
This equipment was used on a mobile home site and led to a fire that killed the occupants in their home!


Attachments:
File comment: No blow “conduit� fuses,
85CB7616-A1C9-407E-A076-9E3EE6CEF574.jpeg
85CB7616-A1C9-407E-A076-9E3EE6CEF574.jpeg [ 83.07 KiB | Viewed 4798 times ]

_________________
Joe Tedesco, NEC Consultant
Top
 Profile  
Reply with quote  
 Post subject: Re: Rigid metal conduit used as fuses
PostPosted: Sat Mar 02, 2019 5:43 pm 
Arc Level
User avatar

Joined: Fri Jul 08, 2016 10:01 am
Posts: 499
:shock: I'm going to ask SKM for the TCC curves on those on Monday to add to my device library.

Seriously though, sad story and totally preventable.

_________________
Retired but I might visit once in awhile


Top
 Profile Send private message  
Reply with quote  
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 2 posts ] 

All times are UTC - 7 hours


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Jump to:  
© 2022-2025 Arcflash Forum / Brainfiller, Inc. | P.O. Box 12024 | Scottsdale, AZ 85267 USA | 800-874-8883