It is currently Mon Nov 02, 2026 11:41 pm
 Post subject: Open Delta in EasyPower
PostPosted: Thu Aug 28, 2008 4:33 pm
Has anyone done a open delta in EasyPower? Support says it can't be modeled but I was wondering if anyone has come with a work around that provides a reasonable answer.
But this may also be a mute point for Arc Flash as it is a txf bank of a 75 & 15 kva txf at 240V. Technically this meets part of the exclusion in IEEE 1584 being less than 125 kva but is not less than 240V.
Thoughts and comments appreciated.
PostPosted: Fri Aug 29, 2008 8:39 am
Probably is not worth considering < 125 kVA but you could perhaps fake it with a three phase which should be worse than your requirement. IEEE 1584 is only for three phase.
